Hi all,

PFA for 2012 module 2 layout attempt.
Please provide your valuable comments for future improvement.

Thanks in advance
Prabhakar
Hi all,

PFA for 2012 module 2 layout attempt and calculation.

Please provide your valuable comments for future improvement.

Thanks in advance.

Prabhakar
Here are some of my thoughts: A word of warning: I am a student preparing for the exam, so no guarantee whatsoever that what I say is in any way correct.

I admit to be somewhat fogged about what the first two operating requirements are trying to get at. If someone could enlighten us it would be useful. As for the third it seems to me to be clearly hinting that signal 217 should have a restricted overlap so that crossover 1104 can remain in use with a train making a station stop. The same applies to the next operating requirement. It is strongly suggesting that there should be a ROL after 225.

On the up fast with the bi-directional signalling I notice that you have not placed track section joints to replace the signal. This is good as they are auto signals. However, the placement of overlaps could be improved. What is the purpose of section BAN? it adds extra joints without any operational benefit. The overlaps from 326 and 419 should be extended so that they share a joint. (I made the same mistake in my attempt at the 2013 paper and Peter pointed it out to me).

Other than S680, none of the signals have junction indicators. Some of the junction protecting signals are lacking any obvious form of junction signalling whilst others have been provided with standard indicators. Standard indicators are fine for lower speeds divergences such as the one into the terminal platform. The UK mainline standard is to use junction indicators for high speed turnouts. Furthermore, I would think that use of flashing yellows over the 100kmh divergences would be suitable.

Prior to connection between the goods line and the platform line trap points are needed for freight traffic.

All trap points should be provided with track circuit interrupters. (though in the case here, the TCs tend to end before the trap points, so not sure what should be done).

Generally, there shouldn't be staggered signals on parallel lines. The signals should be in line with each other which is not the case with 421 and 223. However, it is possible that this rule may be open for relaxation based on a risk assessment. Perhaps a note to show that you are aware of the rule would have been useful.

Some other points:
1) Signal S215 has a subsidiary signal incorrectly drawn with a stop aspect.
2)How come S215 to S214 is not MAR?

Hope this was useful, apologies for any inaccuracies, im in a learner myself!
(18-09-2015, 06:49 AM)prabhakarmishra Wrote: [ -> ]Hi all,

PFA for 2012 module 2 layout attempt and calculation.

Please provide your valuable comments for future improvement.

Thanks in advance.

Prabhakar

Firstly apologies for the length of time taken to look at this;  a period of leave and then a particularly challenging time both at work and domestically has coincided with a flood of last minute interest in exam preparation by quite a few, some contacting via this Forum and others by diverse means and overwhelmed.  Moral students need to start earlier next year!

However looking at calcs, these are good but could be better explained; conversely some of what you spent time on wasn't of great value.  

1. Diagram to explain the derivation of headway formulae more essential than your graph of "braking characteristic" which I don't think adds anythingb and not quite sure what it means anyway

2. worth explaining the conversion factor to m/s; you have just injected 5/18 factors without explaining on first use.

3. Headway calcs are for 120km/h; therefore the freight which only goes at 100km/h cannot be relevant; there is only one of them an hour anyway!

4. Explanation of why you decided upon headway requirement of 225 secs on page 3 was GOOD

5. Further down in explanation re 3 or 4 aspect signalling, generally ok, but should have made clear that 4 aspects can be almost double the price (based on increased number of signals and more separate train detection sections needed per unit length of railway) and so strong incentive only to use 4 aspects when there is tangible benefit of so doing; I don't disagree with overall conclusion though.

6. Treatment of the branch was GOOD, particularly the diagram
You did waste some time because a bit repetitive (figures could have ben reused from page 1; iyt took you some time to realise that the branch had two identical sections and that "ditto" was appropriate.
However you didn't calculate EXACTLY what was needed; you decided that the re-entry time was 922 sec when that was really the time between one train going onto the branch and then getting off again.  You should have added a time (say 40sec) to allow for the point to be freed up after the back of the train has passed clear, then signaller realise, then set a route for train2 onto the branch, the points to move, the signal to clear, the driver to notice, close the train doors, take off the brakes and then apply power and get to the branch points.
Issue is that there is a bare minimum of 16 mins between trains and that for timetabling purposes it could at most sustain 3 trains per hour.  Since in fact there are 2 passenger trains an hour (it does not say but the implication is that it is a half hourly "clockface" service) and a freight also to fit in to the pattern (of course goes beyond B to A and therefore "goes" but does not "come back" or vice versa in any one gap in the passenger service, it could probably just about work as a single block section from E to B.  However may well be worth splitting that into two; in which case the obvious place to put intermediate signals is at station C in both directions of travel.

7. On the last page (which could have done with a heading relating to the rationale for the signalling that you actually intend to use for signallling the layout), it was hood that you clearly presented the minimum and maximum spacing for 3 and 4 aspects (since you have already stated you will deploy 4 aspects in a specific area and 3 aspects elsewhere), but you should have explained where the 1.5 factor came from.  You have just said "assuming 50% margin" when in fact the maximum spacing permitted is based on what it is reasonable amount by which sections may be overbraked before the risk of driver complacency leading to SPAD when a shorter section elsewhere is encountered is assessed as being too high.  You should also have justified that the maximum spacing (in the case of 3 aspects) would actually satisfy the headway constraint as well.
The last paragraph relates to the branch, but as we have stated above few section signals are needed and so the minimum will relate to the braking between the Y/G and the section (R/G) signal and the headway constraint (don't actually need to consider since have effectively already covered in discussion (section 6 above) relates to the separation of the section signals.  Your presentation seems to suggest that you may not have fully comprehended and have just multiplied the min braking distance value by 1.5.

Overall though the calcs were well laid out, clearly legible and understandable; not a bad attempt but attention to the items above would make them even better.
(18-09-2015, 07:14 PM)TheRailwaySignaller Wrote: [ -> ]Here are some of my thoughts: A word of warning: I am a student preparing for the exam, so no guarantee whatsoever that what I say is in any way correct.

I admit to be somewhat fogged about what the first two operating requirements are trying to get at. If someone could enlighten us it would be useful. As for the third it seems to me to be clearly hinting that signal 217 should have  a restricted overlap so that crossover 1104 can remain in use with a train making a station stop. The same applies to the next operating requirement. It is strongly suggesting that there should be a ROL after 225.

On the up fast with the bi-directional signalling I notice that you have not placed track section joints to replace the signal. This is good as they are auto signals. However, the placement of overlaps could be improved. What is the purpose of section BAN? it adds extra joints without any operational benefit. The overlaps from 326 and 419 should be extended so that they share a joint. (I made the same mistake in my attempt at the 2013 paper and Peter pointed it out to me).

Other than S680, none of the signals have junction indicators. Some of the junction protecting signals are lacking any obvious form of junction signalling whilst others have been provided with standard indicators. Standard indicators are fine for lower speeds divergences such as the one into the terminal platform. The UK mainline standard is to use junction indicators for high speed turnouts. Furthermore, I would think that use of flashing yellows over the 100kmh divergences would be suitable.

Prior to connection between the goods line and the platform line trap points are needed for freight traffic.

All trap points should be provided with track circuit interrupters. (though in the case here, the TCs tend to end before the trap points, so not sure what should be done).

Generally, there shouldn't be staggered signals on parallel lines. The signals should be in line with each other which is not the case with 421 and 223. However, it is possible that this rule may be open for relaxation based on a risk assessment. Perhaps a note to show that you are aware of the rule would have been useful.

Some other points:
1) Signal S215 has a subsidiary signal incorrectly drawn with a stop aspect.
2)How come S215 to S214 is not MAR?

Hope this was useful, apologies for any inaccuracies, im in a learner myself!

Only a partial quick reply at present-

1st requirement.
Operating mode 1 is one train is captive on branch using the top platform at station E going via C to B and returning to its platform at E before going back to B.  Splendid isolation from the rest of the railway
Operating mode 2 for a few key hours per day is when a train from B runs through (potentially any one of the platforms at) E and once it has vacated the branch and on its way to H, a different train that has previously come from H is signalled onto the branch at station E and runs via C to B and returns and sometime after it has cleared the branch another fresh train is signalled on to it.

2nd requirement
The Down Fast is to be signalled for both Up and Down direction running, the rationale for which is that it is to be utilised for a non-stop train whilst it is overtaking a slower train stopping at G either on the Down Slow or on the Up Main.
(18-09-2015, 07:14 PM)TheRailwaySignaller Wrote: [ -> ]The third [requirement] seems to me to be clearly hinting that signal 217 should have a restricted overlap so that crossover 1104 can remain in use with a train making a station stop. The same applies to the next operating requirement. It is strongly suggesting that there should be a ROL after 225.

On the up fast with the bi-directional signalling I notice that you have not placed track section joints to replace the signal. This is good as they are auto signals. However, the placement of overlaps could be improved. What is the purpose of section BAN? it adds extra joints without any operational benefit. The overlaps from 326 and 419 should be extended so that they share a joint. (I made the same mistake in my attempt at the 2013 paper and Peter pointed it out to me).

Other than S680, none of the signals have junction indicators. Some of the junction protecting signals are lacking any obvious form of junction signalling whilst others have been provided with standard indicators. Standard indicators are fine for lower speeds divergences such as the one into the terminal platform. The UK mainline standard is to use junction indicators for high speed turnouts. Furthermore, I would think that use of flashing yellows over the 100km/h divergences would be suitable.

Prior to connection between the goods line and the platform line trap points are needed for freight traffic.

All trap points should be provided with track circuit interrupters. (though in the case here, the TCs tend to end before the trap points, so not sure what should be done).

Generally, there shouldn't be staggered signals on parallel lines. The signals should be in line with each other which is not the case with 421 and 223. However, it is possible that this rule may be open for relaxation based on a risk assessment. Perhaps a note to show that you are aware of the rule would have been useful.

Some other points:
1) Signal S215 has a subsidiary signal incorrectly drawn with a stop aspect.
2)How come S215 to S214 is not MAR?

Hope this was useful, apologies for any inaccuracies, im in a learner myself!

Agreed, 
  • 217 does require a ROL so that 415 can be routed from platform 2 to the Down Slow whilst another train enters the platform 3 from the Branch
  • 225 does need a ROL so that a train can be signalled into station G platform with points 1101 Normal for a train to pass on the Down Main
  • It is a common mistake that students place a signal and simply measure 180m and mark an obverlap joint wherever that falls without really thinking. Yes a longer overlap does affect headways, but actually very little effect - typically a few seconds unless the speed is very low.  Even worse than superflous sections (more money to provide,more cost to maintain less reliability) are overlaps that are 180m from signal that fall in silly places within pointwork (e.g. places that are physically impossible, places that are foul unnecessarily etc.)  In fact you should actually think of the various possible places a track joint would be possible and which ones might be a potentially sensible position for an overlap BEFORE finalising the position of a junction protecting signal.  I also noticed that there are several signals provided with overlaps incorrectly as they mean nothing ifthe signal cannot be approached (and indeed are not generally provided unless there is a main aspect signalled move up to the signal).
  • The IRSE examiners do not put information in a question (and that includes notes etc.  on the module 2 layout) without reason; the signalling provided should be appropriate for the junction divergence speeds and yes in this case for UK signalling the junction signal must have a PLJI, MAY-FA approach release and the relevant flashing aspect sequence on approach.
  • Definitely need traps to protect passenger railway from freight lines, siding and any loops (BOTH ends thereof) where unattended vehicles may be left- in this case the connection is "end-on" but yes trap points are needed.  Indeed none of the trap points that have been included are drawn well- it should be clear in which direction they derail and the track circuit interrupter clearly attached to the running edge of the stock rail with a clear gap from the curved stock rail that should look just like a normal point does and indeed be numbered!
    The thing that is wrong is that the track circuits end before the trap points!  For example in the case of station E Up Siding, the end of track circuiting symbol should be just to the left of 501 GPL so that a train passing the signal is immediately being detected and, should the 1106B points not be Reverse, the train wheels then destroy the Track Circuit Interrupter prior to becoming derailed so that the track cannot become clear again even if no longer shunted.
  • Certainly signals should not be staggered unless there is a rational reason!  Not only is there sometimes a risk associated with driver misreading, particularly on curves when the relative position of staggered signals may appear to alter as they are approached, ut just from practical grounds re placing location cases etc. there are disadvantages.  So it is ridiculous that signals such as 219 and 417, neither of whose placement seems in any sense critically constrained are 90m apart.   Conversely signal 205 clearly has to be positioned at the end of the platform at station B and it is important that the overlap of signal 203 must permit the use of 1109 points reverse, so that stagger is inevitable and given the geography and likely speed, there really is no significant risk associated anyway - hence that is perfectly acceptable.
A few further comments:
1. Some of the numbered list of notes provided probably weren't worth writing as they do not really affect the how the layout was signalled.  It does not matter whether the points are operated by HW point machines- the only thing to make clear is if any points are exceptions in that they are
a) operated by immediately adjacent hand levers, or
b) from a Ground Frame facility in the vicinity
and you can do this by symbols.

Similarly other than placing constraints on signal structures and provoking unwanted questions re where any neutral sections are located, specifying that the area is ac electrified really is not significant.

Again by specifying that dc (ac immune) track circuits are provided, all that provokes in my mind is why then you have drawn track section lengths quite a bit longer than could be made to work!  Rather than giving you any marks for specifying, I would be more likely to deduct marks, whereas if you hadn't stated then I'd be reasonably comfortable that track sections might be ok up to around 1000m.

I think notes 4 & 5 were worth making, and I'd also have add that TPWS provided at junction protecting signals. 

However note 6 doesn't really add anything; indeed given that several trap points are not numbered at all and also rather inconsistent numbering of 1107/1108, if I were an examiner I wouldn't be convinced the student actually understood the note and might assume that they had just regurgitated.

Another area where "less is more" would be the marking of the Clearance Points.  The problem is that the vast majority of CPs are marked in places which just would not be clear.  Where tracks are spaced at a nominal 6ft (as one might well assume adjacent tracks would be unless there is any particular evidence to the contrary) then the CP for a crossover would be approximately opposite the switch tips.    I'd be prepared to accept the CPs drawn at 1104 and at 1105 and perhaps 1108 as actually being feasible; the Branch is clearly a fair distance from the Down Main given the island platform 2&3 (similarly the CP for 1110 and the CP for 1101 where the depiction does indeed suggest a relatively wide separation) but all the others scream WRONG.  
I would not mark the obvious CPs at all; just those that are looking marginal and you want to emphasize to the examiner that you consider a particular joint to be clear- however you lose all credibility if you mark things as clear which patently are not.

In a similar vein, you have placed some signal structures between the Down Fast and the Up Main; there wouldn't be space between the tracks to place them like that.  You could have drawn then cantilevered from the cess had you not defined this as ac electrified railway, but since you have then you'd basically need to draw gantries spanning all tracks and the signal heads hanging downwards from it.  Given the wider than nominal spacing of the Down Slow and Down Fast, then I am prepared to believe that signals such as 417 would be possible.

The Branch is quite oversignalled; the calculations suggest that a maximum of 2 block sections needed in each direction.  So 314 at station C would only be a Red/Green and 312 only a Yellow/Green distant for 310 (which actually would be far better positioned at least 300m towards station B).  Signal 316 would just be a Yellow/Green and, if you need it at all, signal 318 would be a Red/Green.
In the other direction, signal 215 would be better placed some 200m closer to station E and a Yellow /Green signal at just about minimum braking distance would be deployed instead of signal 213.  Signal 211 at station C would just be a Red/Green  and similarly would have a Yellow/Green on the approach in lieu of signal 209.  Signal 207 would not be provided.

It was the area approaching the Freight Depot which was the most adrift.  
  • Certainly can't have an auto signal 308 reading over points 1111 and having 1112 in the overlap beyond 306; it also should not have a Green since 306 is a fixed Red with a PL
  • It is not clear where the boundary between the area of control of the main signalbox and whatever controls the Freight Depot actually is; indeed can't even tell which bits of railway are track circuited and which are not
  • Signal 506 seems potentially superfluous and appears not to have any train detection, reads through a set of gates blocking the railway but appears to have a route indicator presumably selected on the lie of a set of handpoints that do not seem to be electrically detected- so it looks a mess!
  • If we envisage a freight train hauled to 306, the locomotive then uncoupled from its train and then signalled via 306's PL whilst its wagons are left on the running line, we then have a PL on 201 to signal it into the Run-round line, so this is all good so far.  The loco can then run ll the way into the neck and be signalled back onto its train using 505; I'd have expected it to the left of the line, but I suppose if the driver is actually permitted to get back onto the train driving from the furthest cab (but see later!) I suppose it could make sense to have this between the tracks (but still does not excuse the signal being drawn on its side!).  Certainly the runround move is possible (but there is no way of signalling in/ out of the little siding should there be a need to leave a vehicle there and therefore this area incomplete) and the train is ready to be propelled into the depot.  
  • If the driver is in the cab from which he could have seen 505 as drawn, then not going to be able to see 306 PL- it's 400m away and on the other side of the line with the train blocking any visibility.  Need to think carefully about how this area would be operated and then add some notes to explain whilst making sire that the signalling shown on the plan is compatible.  Propelling a long freight train always has its risks; when the signals are GPLs and there is a set of gates that need to be opened from being across the line and handpoints involved,if not careful it is an accident waiting to happen!
  • Similar considerations apply to train leaving the depot; what controls would actually be in those GPLs at end of yard sidings, who controls them etc?
This whole area suggests that the candidate does not really understand this type of operation at all, so wouldn't be getting good marks here, but on the other hand  you'd get some credit for at least basically being able to run around the train.  

Actually I think that rather less controlled signalling here is the answer; 1111 and 1112 should be operated by train crew via a Ground Frame, perhaps released by train staff and many of the movements being authorised by the guard trackside at one extremity of the train via a back-back radio to the driver at the other.


So there is quite a lot that could have been better in many respects on this layout; however I have actually seen quite a bit worse and it is substantially complete.  There are some things that particularly detract:
  • CPs
  • Overlaps
  • Route Indicators
  • Trap points and TCIs
  • Signals on wrong side of line / between tracks where couldn't fit
Even given the now very limited time before the exam, these above faults shouldn't be impossible to rectify and if you can eliminate them then you'll probably pass the module but rather close for comfort I think.  Less of the standard notes that aren't going to score you much, more route boxes and even if you don;t name every track section, at least be clear which areas are and which are not track circuited.
(25-09-2015, 07:46 PM)PJW Wrote: [ -> ]
  • none of the trap points that have been included are drawn well- it should be clear in which direction they derail and the track circuit interrupter clearly attached to the running edge of the stock rail with a clear gap from the curved stock rail that should look just like a normal point does and indeed be numbered!
  • Another area where "less is more" would be the marking of the Clearance Points.  The problem is that the vast majority of CPs are marked in places which just would not be clear.  Where tracks are spaced at a nominal 6ft (as one might well assume adjacent tracks would be unless there is any particular evidence to the contrary) then the CP for a crossover would be approximately opposite the switch tips.    I'd be prepared to accept the CPs drawn at 1104 and at 1105 and perhaps 1108 as actually being feasible; the Branch is clearly a fair distance from the Down Main given the island platform 2&3 (similarly the CP for 1110 and the CP for 1101 where the depiction does indeed suggest a relatively wide separation) but all the others scream WRONG.  I would not mark the obvious CPs at all; just those that are looking marginal and you want to emphasize to the examiner that you consider a particular joint to be clear- however you lose all credibility if you mark things as clear which patently are not.


Here attached is an example extract of the layout showing what I mean for the correct depiction of Clearance Points, trap points and TCI
Hi,
Thank you all for your comments. It is very useful.
There was some doubt regarding clearance points and providing signal between two running lines. Now it is clear.

I agree that driver will not be able to see 306 PL (about 400m away!) and the option of having less controlled signalling here.
But ( just curiosity) can you suggest a way to (controlled) signal train movement after run round into siding?
Is option of providing another GPL near 1111B is suitable?
What are those risks that you want us to focus ?
"Propelling a long freight train always has its risks; when the signals are GPLs and there is a set of gates that need to be opened from being across the line and handpoints involved,if not careful it is an accident waiting to happen!"

I'm new in this field. Apologies if I asked some thing obvious .

Thanks
Prabhakar
(30-09-2015, 09:49 AM)prabhakarmishra Wrote: [ -> ]Hi,
Thank you all for your comments. It is very useful.
There was some doubt regarding clearance points and providing signal between two running lines. Now it is clear.

I agree that driver will not be able to see 306 PL (about 400m away!) and the option of having less controlled signalling here.
But ( just curiosity) can you suggest a way to (controlled) signal train movement after run round into siding?
Is option of providing another GPL near 1111B is suitable?
What are those risks that you want us to focus ?
"Propelling a long freight train always has its risks; when the signals are GPLs and there is a set of gates that need to be opened from being across the line and handpoints involved,if not careful it is an accident waiting to happen!"

I'm new in this field.  Apologies if I asked some thing obvious .

Thanks
Prabhakar

Unless the running lines are widely spaced (for example there is generally a "10 foot" between each pair of tracks on a 4 track railway, then there isn't the clearance for a straight post signal.  In the UK the only signals placed between normally spaced running lines have to fit within the "915mm high above rail height" space within the structure gauge; in practice this means a GPL signal with a route indicator or a ground mounted main 3 aspect signal head (rare but occasionally used from exit of sidings or terminal platforms or as a co-actor associated with a normal main signal).

Yes you could provide more signals to allow a signalled run-round move.  
  • If (over)signalling this area, I'd have placed 308 (but only a Red/Yellow) at about the "0900" datum (even if giving an overlap on a Goods line it wouldn't be restrictive since there can be no other train in the area!); braking isn't an issue since only 40km/h
  • 306 would be almost as you had drawn it- you could get a ground mounted red main aspect with PL above it between the line and the loop.  At 40km/h it would be ok when loco pulling its train; the problem is the PL visibility after the loco has run around and is pushing the 400m train.  You'd probably have to put a couple of banners  for the Up direction placed to the right (i.e. above the line on the plan) of the Goods line; indeed it may be best to have placed 306 as a normal straight post on this "wrong" side of the line as well. However this would then require the driver to do the setback move from the furthest end driving cab not only propelling their train but with neck contorted looking back over their shoulder out of the window as well; not only would they be able to see very little of use but it would be most uncomfortable and a distraction- this would be for the length of the movement which must be some 1200m and that is going to take perhaps 3-4 minutes, so NOT A GOOD IDEA! The alternative of cantilevering 306 and its banners over from the cess of the runround loop would add tremendously to costs- all ready very high for what is a one freight per hour service.  
    [As I said before I'd not signal it; I'd use the guard with a radio link to the driver, but you did ask........]
  • 201 would be as you had drawn it but without the Auto facility!.  
  • You'd need a GPL at the tips of 1112A to be able to get into siding (the loco would have obviously to be to the right of the wagon(s) so perhaps it is one that has been extracted from a train being shunted within the yard sidings).  Also need a GPL (broadly opposite 201) to get out of that siding again.
  • There is probably little value in a signal at datum "0780" as 201B(S) may as well read to the buffers in the neck, but you would need GPL 505 to route back onto the Goods line
  • If you provided GPL 506 to give a signalled move into the yard, then you should at very least detect the gates open but probably also lock them open whilst that route was set, so that would need to be depicted, perhaps as a gatelock instrument.
  • Alternatively you would probably be better to define the 306 PL to read only as far as a red roundel mounted on the gates themselves (no overlap!) and make it handsignalling from that boundary- but actually I would have provided a "STOP and Wait Instructions" reflectorised board just prior to those gates in lieu of GPL 506.  
  • Similarly in the opposite direction would provide such STOP boards at the exit of each siding (in lieu of the unidentified GPLS on your plan) and authorise verbally the driver to pass over handpoints, through the gates up to the main signalbox's first signal 201.  However there would need to be some means of ensuring that the yard shunter was not authorising a train to leave at the same time that the signaller was routing one in the oposite direction. so some form of shunter's acceptance input into the main signalling system to make sure that there was not "a proper misunderstanding" could occur.

However I think that the run round would best be controlled locally 
  • control the points from mechanical levers of Ground Frames [#] positioned at each end of the loop, released by a Train Staff (or similar) which is what authorised the freight train to enter the last portion of the line beyond station B.  
  • these mechanical levers would be operated by the train's guard who could then go on foot to open the gates, operate handpoint within the yard sidings and check the siding ready to receive the train.  From there they could use the radio to continually assure the driver that they should be continuing to propel their train and then walk alongside the rear of the train as it gets pushed into a siding in order to give appropriate warning to the driver prior to the position to stop.
  • would then walk up the side of the train, uncouple the loco, verbally authorise towards the gate, change the handpoint, authorise the driver towards them and come next to the other rake of vehicles and then couple to them.
[#] actually the point ends at the "0800" datum could actually be spring points- the end in the neck always directing facing move towards the Goods line and the end on the Goods line always routing facing moves to the Down Goods. The guard would not then have to walk the 400m there and then 400m back again to operate the second GF; as soon as the loco had passed clear of the "0360" datum crossover in the reverse lie and proceeding along he Run Round line, the guard could normalise those points and be getting the yard ready for the propelling move whilst loco completing the runround move- the only thing is that they'd probably still have to talk the length of the train to couple up again, so don't really save much .time


No question is too obvious to be worth asking